A collection of the PDF presentation published at the Clean Energy Council (CEC) Wind Forum 2016 in Melbourne. Key issues discussed were colocation of wind and solar, noise impacts, planning requirements across Australia and developments in the technology.
2. Wind Power Plant Frequency Control to Support the
Penetration of High Levels of Renewable Sources
[17 March 2016, Antonio Martinez, Kouroush Nayebi, Manoj Gupta, Yi Zhou, Vestas Wind Systems A/S]
Wind Industry Forum, 17 March 2016
PUBLIC
3. Agenda
Wind Power Plant Frequency Control to Support the Penetration of High Levels of Renewable Sources2
Overview of Frequency Control and Regulation
Frequency Control Challenges with High Levels of Renewables
Frequency Control Support from Wind Power Plants
Inertia Emulation Control (FUTURE)
Active Power Control
Frequency Control
Fast Power De-rating
Conclusions and Recommendations
4. Overview of Frequency Control and Regulation
Wind Power Plant Frequency Control to Support the Penetration of High Levels of Renewable Sources3
Frequency Response
• Balancing supply and demand
Frequency
(Hz)
Time
(Seconds)
Primary Frequency Control
Inertial Response
Secondary Frequency Control
Recover frequency to 50 Hz:
·
WPP frequency control
·
WPP active power control
·
5 minute contingency FCAS
·
Automatic Generation Control (AGC)
·
Manual dispatch commands
50 Hz
0
secs
Typically
5-10 secs
Typically
20-60 secs
Typically
5-10 mins
Stabilize frequency:
·
WPP fast power control
·
WPP fast frequency control
·
60 second contingency FCAS
·
Governor response
Stabilize df/dt and df:
·
WPP Inertia Emulation Control (FUTURE)
·
6 second contingency FCAS
·
Generator inertial response
fnadia
Frequency
Regulation
Control
Frequency Regulation to 50 Hz:
·
WPP active power control
·
Regulation FCAS
5. Frequency Control Challenges with High Levels of Renewables
Displacement of
synchronous
generators
Reduced
system inertia
Rapid changes
in frequency
(larger df/dt)
Synchronous
generator
tripping on df/dt
Larger
frequency
deviations
(larger df)
Increased risk
of UFLS
Power forecasting
for Wind and PV
generation
Supply and
demand
balancing
Wind Power Plant Frequency Control to Support the Penetration of High Levels of Renewable Sources4
6. Frequency Control Support from Wind Power Plants
Inertia Emulation
Control (FUTURE)
Potential Benefits
Increased system
inertia for raise
services
Slower changes in
frequency (reduces
df/dt)
Reduced
Synchronous
generator tripping
on df/dt
Smaller frequency
deviations (smaller
df)
reduced risk of
UFLS
Allows time for
governors to
respond
ROCOF and
Frequency Withstand
Capability Benefits
(typ. 1-4 Hz/sec)
WPP ROCOF
withstand-reduced
tripping (1-4
Hz/sec)
WPP frequency
withstand-reduced
tripping (47-53Hz
continuous)
No added
contribution from
WPP to frequency
deviation
Fast Frequency
Control and Fast
Power De-rating
Benefits
Raise and lower
contingency FCAS
services (6s, 60s)
Slower changes in
frequency (reduces
df/dt)
Reduced
Synchronous
generator tripping
on df/dt
Smaller frequency
deviations (smaller
df)
reduced risk of
OFGS, UFLS
Allows time for
governors to
respond
Fault Ride Through
Capability Benefits
No WPP tripping-no
added contribution
to frequency
deviation
Fast post-fault
active power
recovery-contribute
to stabilising
frequency
Frequency Control
Benefits
Raise and lower
contingency FCAS
services (60s,
5mins)
Active Power Control
Benefits
Raise and lower
Regulation FCAS
Wind Power Plant Frequency Control to Support the Penetration of High Levels of Renewable Sources5
Benefits
Frequency
(Hz)
Time
(Seconds)
Primary Frequency Control
Inertial Response
Secondary Frequency Control
Recover frequency to 50 Hz:
·
WPP frequency control
·
WPP active power control
·
5 minute contingency FCAS
·
Automatic Generation Control (AGC)
·
Manual dispatch commands
50 Hz
0
secs
Typically
5-10 secs
Typically
20-60 secs
Typically
5-10 mins
Stabilize frequency:
·
WPP fast power control
·
WPP fast frequency control
·
60 second contingency FCAS
·
Governor response
Stabilize df/dt and df:
·
WPP Inertia Emulation Control (FUTURE)
·
6 second contingency FCAS
·
Generator inertial response
fnadia
Frequency
Regulation
Control
Frequency Regulation to 50 Hz:
·
WPP active power control
·
Regulation FCAS
7. 6
Inertia Emulation Control (FUTURE)
• Kinetic energy is extracted from all the WTG rotating masses (blades, rotor, gearbox, etc) to produce
active power
• Controlled active power production is possible beyond the available power from the wind
• Trigger: ROCOF threshold, ferror threshold or both
• ∆Pinertia: Requested power change in % of Prated for a predefined duration in seconds.
Concept Description
Wind Power Plant Frequency Control to Support the Penetration of High Levels of Renewable Sources
• Allows time for the governors to respond to stabilise
frequency
• Further research into the benefits of emulated inertia
control from WPP is required
Frequency
Monitoring
&
Conditioning
Rate of change
of frequency
(ROCOF)
Estimator
Delta Power
calculator
Inertial
responce trigger
ferror
ROCOF
ferror
fmeas
Trigger
+DPinertia
P actual
Power output
8. 7
Inertia Emulation Control (FUTURE)
Tdelay: Adjustable initial delay.
Trise: The time it takes to reach the needed boost level. The rate of power change is adjustable.
Tsustain: Adjustable maximum boosting time.
Conceptual Response
Wind Power Plant Frequency Control to Support the Penetration of High Levels of Renewable Sources
9. 8
Active Power and Frequency Control
Power Plant Controller® (PPC) Architecture
Wind Power Plant Frequency Control to Support the Penetration of High Levels of Renewable Sources
Frequency
Controller
Option 1
-
Set-Point Frequency
Measured Frequency
Frequency Controller (I)
Active
Power
Dispatcher
Active Power
Reference
WTGs
& or
Pause / Stop
Dispatcher
Power
Controller
Power Control
Curtailed Power
WTGs power
production
Frequency
Controller
Option 2
Available Power
FRT Mode
FRT Mode
Inner Control Loop
Outer Control Loop
Signal
Conditioning
Power Setpoint
Power limit
Power limit
FRT Mode
Power limit
-
Fast Run-back
High Frequency limit
Fast run-back
FRB set by TSO
Power set point for FRB by TSO
Trip commands to
Feeder CBs
Options or Modes
Frequency Controller (II)
Power reference
Active Power loop
Operation Mode
Measured/Calculated Power
Measured/Calculated Power
Measured/Calculated Power
Measured/Calculated Power
Set-Point Frequency
Measured Frequency
Curtailed Power
Measured Frequency
Available Power
10. Active Power Controller
The active power controller controls the active power output of the wind power plant (WPP).
The active power reference can be provided by different sources.
• Fixed external/internal level
• Frequency Controllers
• Fast Runback Controller
The controller determines active power set-points for the individual turbines in its dispatcher.
The controller includes the following functions:
• Curtailment by a fix value below available
• Curtailment by % of available below available
• Curtailment Ramp rate limiter
• Power Increase Power Ramp rate limiter
• Pausing and releasing WTGs
• Tripping Feeders for fast power reduction
Wind Power Plant Frequency Control to Support the Penetration of High Levels of Renewable Sources9
Primary, Secondary Frequency Control and Frequency Regulation
11. 55
57
59
61
63
65
67
69
71
73
75
0 10 20 30 40 50 60
Time [s]
Power[MW]
Pref
Pmeas
Ppossible
-2
-1
0
1
2
3
4
5
6
0 10 20 30 40 50 60
Time [s]
Powerreduction[MWbelowPpossible]
45
47
49
51
53
55
57
59
61
63
65
0 10 20 30 40 50 60
Time [s]
Power[MW]
Pref
Pmeas
Ppossible
88
89
90
91
92
93
94
95
96
0 10 20 30 40 50 60
Time [s]
PowerProduction[%ofPpossible]
Onsite Active Power Control Performance
Wind Power Plant Frequency Control to Support the Penetration of High Levels of Renewable Sources10
De-rated operation for raise and lower frequency control services
• Power Reference is set to 92% of possible power
• Power Reference is set to 4 MW below possible power
12. Over Frequency
Support
Under Frequency
Support
Frequency Control Option 1
• Support to stabilize frequency and to recover frequency to 50 Hz.
• Droop control focuses on changing (Raise or Lower) the active power (dP) proportional to the grid
frequency deviation (df).
• The frequency deviation (df) is the difference between the grid and reference frequency.
Wind Power Plant Frequency Control to Support the Penetration of High Levels of Renewable Sources11
Primary and Secondary Frequency Control
13. 70
71
72
73
74
75
76
77
78
79
80
0 5 10 15 20 25 30 35
Time [s]
Power[MW]
Pref
Pmeas
1,002
1,003
1,004
1,005
1,006
1,007
1,008
1,009
0 5 10 15 20 25 30 35
Time [s]
Frequency[p.u.]
Fmeas
68
70
72
74
76
78
80
82
0 10 20 30 40 50
Time [s]
Power[MW]
Pref
Pmeas
0,998
1
1,002
1,004
1,006
1,008
1,01
1,012
0 10 20 30 40 50
Time [s]
Frequency[p.u.]
Fmeas
Onsite Frequency Control Option 1 Performance
Wind Power Plant Frequency Control to Support the Penetration of High Levels of Renewable Sources12
• Simulated Open-loop frequency offset by 0.01 pu
• Tested with curtailed WPP at 80 MW in FSM mode
• Simulated open-loop frequency step from 1.0083 pu to 1.003 pu
• Tested with curtailed WPP at 80 MW in FSM mode
14. Frequency Control Option 2
• This type of frequency control follows available power in the wind at all times by an offset in MW of in % of
available to allow for raise services.
• Controller uses the available power at time of frequency error observation to lower or raise the power
during frequency contingency.
Wind Power Plant Frequency Control to Support the Penetration of High Levels of Renewable Sources13
Primary and Secondary Frequency Control
Under
Frequency
Support
Over
Frequency
Support
15. Onsite Frequency Control Option 2 Performance
• Simulated Open-loop frequency
• Comparing the measured power and the measured control settings
Wind Power Plant Frequency Control to Support the Penetration of High Levels of Renewable Sources14
Primary and Secondary Frequency Control
16. Fast Power De-rating
Wind Power Plant Frequency Control to Support the Penetration of High Levels of Renewable Sources15
Primary Over Frequency Control
• Fast Power reduction to a predefined
level by TSO.
• Fast Power reduction by monitoring
frequency
P Dispatcher
FRB power command
FRB flag
Measured Active Power
FRB
Reference
Calculation
Pref_FRB FRB_Flag
Pref
Psetpoint_WTG
TRIP
Selector
TRIP_Feeder
Fast Runback Controller
WTG
power
Feeder
WTG list
Psetpoint_PPC
DP
P Dispatcher
Measured Frequency
Measured Active Power
Psetpoint_WTG
TRIP
Selector
TRIP_Feeder
Fast Frequency Controller
WTG
power
Feeder
WTG list
Psetpoint_PPC
DP
0
20
40
60
80
100
120
46 48 50 52 54
Power[%ofnominal]
Frequency [Hz]
frequency/Power Curve
17. Conclusions and Recommendations
Conclusions:
• WPP can provide important contingency and regulation FCAS services to manage the system frequency.
• Today WPPs can provide primary frequency control, secondary frequency control and frequency regulation,
in a similar way (or better) to synchronous generators.
• In the future WPPs may have emulated inertia control capability, however, the benefits are yet to be
understood for various types of grids and operational issues
Recommendations for the future:
• Consider market side solutions to manage the system frequency with high levels of renewables. For
example:
• Introduce incentives for WPP to enter the FCAS markets
• Network upgrades (e.g. new lines or interconnectors)
• Review of the system frequency operating standards
• Procuring more FCAS during low inertia operation or other high risk operational scenario (high risk of large supply and
demand imbalance)
• Improve the power forecasting and the dispatching of WPP
• Reduce/eliminate non-scheduled generation
• Further research into the benefits of emulated inertia control from WPP is required
Wind Power Plant Frequency Control to Support the Penetration of High Levels of Renewable Sources16
20. •Wind farm noise often less than ambient noise
•Makes compliance monitoring difficult
•No single definitive objective method of monitoring
•Has recently become controversial
•Most common method is:
– Long term logging
– Line of best fit
– Use of LA90
Context
24. Compliance test plan can:
•Simplify conditions of approval
•Define data requirements
•Allow frequency spectrum analysis
•Allow consideration of upwind v downwind
•Allow measurement at intermediate location
•Define tonality
•Define on/off test (last resort)
To improve accuracy
32. • Compliance monitoring is difficult
• Significant risk of false conclusions
• Consideration should begin at application stage to
minimise unworkable conditions
• Methodologies are available to minimise risks
Summary
34. Content of typical planning conditions
Applicable noise standard
Noise limits at receptor locations
Relevant receptor locations
Potential penalties for SACs at receptor locations
2
35. Purpose of noise specification
Compliance with the planning conditions
Quantify allowable noise and character from the
supplied turbine
Methodology and location for quantifying noise and
character
3
37. Risk assessment
Risk of non-compliance with planning conditions
• Operator credibility
• Community impact
• Operator vs. supplier liability
Risk of lost energy yield
5
38. Factors influencing risk
Wind farm size
Distance to dwellings
Topography
Background noise environment
Turbine sound power data
Prediction software and methodology implementation
6
39. Factors influencing risk
Turbine sound power data
• Estimated values
• Test report values with or without uncertainties (IEC 61400-11)
• Guaranteed values
• Declared values (IEC 61400-14)
Octave band spectral content
7
40. Factors influencing risk
Prediction method
• ISO 9613-2:1996 (International Standard)
• CONCAWE (1980s UK research study)
• Nord2000
Method implementation
• Acoustic prediction software (SoundPlan, CadnaA, etc.)
• Wind farm design software (windPRO, WindFarm, etc.)
8
41. Assessment options
Sound power level
+ High signal/noise ratio
+ Well defined methodology (high repeatability)
+ Early evaluation
+ Within the wind farm site
- Not representative of receptor location
- Only representative of the tested turbine(s)
9
42. Assessment options
Receptor location
+ Community involvement
+ Readily comparable with noise limits
- Generally low signal/noise ratio
- Background noise influence
- Potential access issues
10
43. Assessment options
Intermediate location
+ High signal/noise ratio
+ Accounts for influence of multiple turbines
+ Can be within the wind farm site
+ Established method for general environmental noise
- Requires extrapolation to receptor location
11
44. Quantification of A-weighted noise levels
Avoid procedural ambiguities
• Compliance with regulation vs. compliance with defined values
Define measurement methodology
Consideration of uncertainty
• Measured level + uncertainty vs. guaranteed level
• IEC 61400-11 vs. IEC 61400-14
Specification of octave band value
12
45. Quantification of noise character
Definition of relevant characteristics
Avoid procedural ambiguities
• Subjective vs. objective (NZS 6808:1998)
• Presence vs. prominence
Define the relevant assessment methodologies
• Absence of reliable methods for certain characteristics
• C-weighted noise levels (NSW / QLD)
13
48. • Outline of the error
• Outline of AWEFS and UIGF calculation
• Determining Constraint Status of the Wind
Farm
• Market Impact – Example of Lake Bonney
• Market Impact – NEM Wide
• Proposed Solutions
2
Presenters:
Claudia Williams OCC Team Lead
ABOUT INFIGEN
Infigen Energy (Infigen) is a developer, owner and
operator of renewable energy generation in Australia.
We own six wind farms and a solar farm with a
combined installed capacity of 557 megawatts
operating in New South Wales, South Australia and
Western Australia.
Infigen’s operating assets generate enough power to
meet the needs of over 250,000 homes saving over a
million tonnes of carbon dioxide emissions each year.
Infigen’s development pipeline comprises
approximately 1,100 megawatts of large-scale wind and
solar projects spread across five states in Australia.
For further information please visit our website:
www.infigenenergy.com
49. 3
AWEFS and the UIGF
Wind farm
NEMDE
AWEFS
Wind farm SCADA
Data
Price data
Network
Constraint Data
UIGF
Dispatch
targets
50. Dependent on passing the following through checks:
1. Is the wind farm control system setpoint < registered capacity of the wind farm?
2. Is the Wind farm control system setpoint < active power + 5% of registered capacity?
3. Is the wind farm control system setpoint < potential power?
Definitions:
Control System Setpoint (MW): The lowest current set point active on the wind farm at
the time AEMO takes its readings.
Active Power (MW): The current output of the wind farm when AEMO takes its readings.
Potential Power (MW): Possible production of the wind farm AEMO takes its readings.
Determining Constraint Status of Wind Farm
4
3 Validation Checks
54. Market Impacts
4
From AEMO’s scheduling error report, February 2016.
• Assessment Period: 14 March 2012 and 21 November 2015
• 35,589 affected intervals during the assessment period across
at least 19 wind farms
• 54,076 MWh lower due to this scheduling error
NEM Wide
55. 9
Proposed Solutions
• Increase buffer from 5% to higher value
• Buffer value adjusted based on
historical analysis of the wind farm
• Implemented on 3rd February 2016
• Expected to reduce but not eliminate
oscillating constraints
Interim Resolution Permanent Resolution
• Proposed solution to be fully implemented by
June 2016, with changes made by April .
• Introduce link between AEMO Market
Systems and AWEFS on the dispatch time
frame to directly communicate the SDF status
of wind farm to AWEFS
• Introduce semi-dispatch flag into AWEFS to
determine if the wind farm is constrained
• If the park is unconstrained, take the max of
the active power generation and the wind
speed forecast method to produce UIGF
57. Disclaimer
This publication is issued by Infigen Energy Limited (“IEL”), Infigen Energy (Bermuda) Limited (“IEBL”) and Infigen Energy Trust (“IET”), with Infigen
Energy RE Limited (“IERL”) as responsible entity of IET (collectively “Infigen”). Infigen and its related entities, directors, officers and employees
(collectively “Infigen Entities”) do not accept, and expressly disclaim, any liability whatsoever (including for negligence) for any loss howsoever arising from
any use of this publication or its contents. This publication is not intended to constitute legal, tax or accounting advice or opinion. No representation or
warranty, expressed or implied, is made as to the accuracy, completeness or thoroughness of the content of the information. The recipient should consult
with its own legal, tax or accounting advisers as to the accuracy and application of the information contained herein and should conduct its own due
diligence and other enquiries in relation to such information.
The information in this presentation has not been independently verified by the Infigen Entities. The Infigen Entities disclaim any responsibility for any
errors or omissions in such information, including the financial calculations, projections and forecasts. No representation or warranty is made by or on
behalf of the Infigen Entities that any projection, forecast, calculation, forward-looking statement, assumption or estimate contained in this presentation
should or will be achieved. None of the Infigen Entities guarantee the performance of Infigen, the repayment of capital or a particular rate of return on
Infigen Stapled Securities.
IEL and IEBL are not licensed to provide financial product advice. This publication is for general information only and does not constitute financial product
advice, including personal financial product advice, or an offer, invitation or recommendation in respect of securities, by IEL, IEBL or any other Infigen
Entities. Please note that, in providing this presentation, the Infigen Entities have not considered the objectives, financial position or needs of the recipient.
The recipient should obtain and rely on its own professional advice from its tax, legal, accounting and other professional advisers in respect of the
recipient’s objectives, financial position or needs.
This presentation does not carry any right of publication. Neither this presentation nor any of its contents may be reproduced or used for any other
purpose without the prior written consent of the Infigen Entities.
IMPORTANT NOTICE
Nothing in this presentation should be construed as either an offer to sell or a solicitation of an offer to buy Infigen securities in the United States or any
other jurisdiction.
Securities may not be offered or sold in the United States or to, or for the account or benefit of, US persons (as such term is defined in Regulation S under
the US Securities Act of 1933) unless they are registered under the Securities Act or exempt from registration.
96. Overview
Wind and solar co-location
1. The idea
2. Benefits and challenges
3. Complementary nature wind and solar resource
4. System sizing and curtailment
5. Heat map and wind farm ranking
6. Summary
98. 2. Benefits and challenges
Benefits
Benefits
Development cost
Land
Grid connection
PPA
Construction time
O&M facilities
Administration
Additional savings can be
obtained when developing
wind and solar power
plants at the same time as
a greenfield development.
99. 2. Benefits and challenges
Challenges
Challenges
Land use
Sizing & Curtailment
Agreements (GCA, PPA, LPA, O&M)
O&M activities
Community
Selected 10 wind farms for analysis
State Wind Farm
Capacity
(MW)
Yrs of data
available
1 NSW Capital 140 4
2 NSW Gunning 47 3
3 SA Waterloo 111 4
4 SA Snowtown 99 4
5 SA Hallett 1 95 4
6 VIC Waubra 192 4
7 VIC Oaklands Hill 67 3
8 WA Collgar 206 3
9 WA Alinta 89 4
10 WA Emu Downs 80 4
100. 3. Complementary nature of solar and wind
Time of day analysis
Alinta, WA Snowtown, SA
Average annual profile of two wind farms (2011 – 2014)
Conclusions from the
10 wind farms
analysed:
• 6 showed reasonable
anti-correlation
• Strongest anti-
correlation results in
WA
• Large differences
between and also
within states
101. 3. Complementary nature of solar and wind
Time of day analysis
Waubra, VIC Collgar, WA
Average seasonal profile of two wind farms (2011 – 2014)
Conclusions from the
10 wind farms
analysed :
• 6 generated more in
Spring
• 2 generated more in
Summer but showed
dips during daylight
hours
• 2 generated more in
Winter (both in WA)
102. 4. System sizing and curtailment
Curtailment analysis
Solar PV curtailment versus additional solar capacity on each analysed wind farm (2011 – 2014)
100%
25 – 50%
27% curtailment
at Snowtown
Conclusions from the 10 wind
farms analysed :
- Snowtown and Hallett wind
farm show high curtailment
mainly due to its high
generation during the day time
- Suitable penetration with 25%-
50% of solar @5% curtailment
- Curtailment did not exceed
30% when adding 100% of
solar PV.
103. 4. System sizing and curtailment
Overview
(2) Capacity factors are analysed over the years and
are not altered for maintenance or downtime
+11%
104. 5. Heat map and wind farm ranking
Solar and Wind capacity factor map
Filters:
- Wind capacity factor
>35%
- Solar capacity factor
>16%
- Solar farm at 35% of
the capacity of the
wind farm
105. 5. Heat map and wind farm ranking
Ranking of existing wind farms
0.90
0.95
1.00
1.05
1.10
1.15
1.20
0.75 0.85 0.95 1.05 1.15 1.25 1.35 1.45 1.55
CostIndex
Revenue Index
New South Wales South Australia Tasmania Victoria Western Australia
Conclusions:
- Western Australia
provides significant
opportunities
- Victoria and New
South Wales appear
to provide cost
advantages
106. Availability of wind
and solar resource
Complementary
profile of wind and
solar generation
Cost savings
Revenue
opportunities
Agreements and
regulations
6. Summary
Success factors and conclusion
• Our study demonstrates that co-location is
worth the consideration of developers and
existing wind farm owners/operators.
• We encourage developers to consider
both wind and solar for their respective
sites (operational or in development)
• The report is made available on:
http://arena.gov.au/resources/wind-solar-co-
location-study/
109. Overview
Wind and solar co-location
1. The idea
2. Benefits and challenges
3. Complementary nature wind and solar resource
4. System sizing and curtailment
5. Heat map and wind farm ranking
6. Summary
111. 2. Benefits and challenges
Benefits
Benefits
Development cost
Land
Grid connection
PPA
Construction time
O&M facilities
Administration
Additional savings can be
obtained when developing
wind and solar power
plants at the same time as
a greenfield development.
112. 2. Benefits and challenges
Challenges
Challenges
Land use
Sizing & Curtailment
Agreements (GCA, PPA, LPA, O&M)
O&M activities
Community
Selected 10 wind farms for analysis
State Wind Farm
Capacity
(MW)
Yrs of data
available
1 NSW Capital 140 4
2 NSW Gunning 47 3
3 SA Waterloo 111 4
4 SA Snowtown 99 4
5 SA Hallett 1 95 4
6 VIC Waubra 192 4
7 VIC Oaklands Hill 67 3
8 WA Collgar 206 3
9 WA Alinta 89 4
10 WA Emu Downs 80 4
113. 3. Complementary nature of solar and wind
Time of day analysis
Alinta, WA Snowtown, SA
Average annual profile of two wind farms (2011 – 2014)
Conclusions from the
10 wind farms
analysed:
• 6 showed reasonable
anti-correlation
• Strongest anti-
correlation results in
WA
• Large differences
between and also
within states
114. 3. Complementary nature of solar and wind
Time of day analysis
Waubra, VIC Collgar, WA
Average seasonal profile of two wind farms (2011 – 2014)
Conclusions from the
10 wind farms
analysed :
• 6 generated more in
Spring
• 2 generated more in
Summer but showed
dips during daylight
hours
• 2 generated more in
Winter (both in WA)
115. 4. System sizing and curtailment
Curtailment analysis
Solar PV curtailment versus additional solar capacity on each analysed wind farm (2011 – 2014)
100%
25 – 50%
27% curtailment
at Snowtown
Conclusions from the 10 wind
farms analysed :
- Snowtown and Hallett wind
farm show high curtailment
mainly due to its high
generation during the day time
- Suitable penetration with 25%-
50% of solar @5% curtailment
- Curtailment did not exceed
30% when adding 100% of
solar PV.
116. 4. System sizing and curtailment
Overview
(2) Capacity factors are analysed over the years and
are not altered for maintenance or downtime
+11%
117. 5. Heat map and wind farm ranking
Solar and Wind capacity factor map
Filters:
- Wind capacity factor
>35%
- Solar capacity factor
>16%
- Solar farm at 35% of
the capacity of the
wind farm
118. 5. Heat map and wind farm ranking
Ranking of existing wind farms
0.90
0.95
1.00
1.05
1.10
1.15
1.20
0.75 0.85 0.95 1.05 1.15 1.25 1.35 1.45 1.55
CostIndex
Revenue Index
New South Wales South Australia Tasmania Victoria Western Australia
Conclusions:
- Western Australia
provides significant
opportunities
- Victoria and New
South Wales appear
to provide cost
advantages
119. Availability of wind
and solar resource
Complementary
profile of wind and
solar generation
Cost savings
Revenue
opportunities
Agreements and
regulations
6. Summary
Success factors and conclusion
• Our study demonstrates that co-location is
worth the consideration of developers and
existing wind farm owners/operators.
• We encourage developers to consider
both wind and solar for their respective
sites (operational or in development)
• The report is made available on:
http://arena.gov.au/resources/wind-solar-co-
location-study/
121. Nacelle mounted LiDAR
Optimization of the wind farms performance
Melbourne – 17/03/2016 – Wind Industry Forum 2016
Julien Léon
DEWI / UL
Technical Due Diligence – Team Leader France
122. Introduction of UL/DEWI
A Global Service Provider serving the Wind Energy Industry
Global Wind Energy Services
Combining technical expertise with many
years of in-depth industry experience, the
DEWI Group (a UL company) offers global,
one-stop wind energy services to turbine
manufacturers, component manufacturers,
All-in-One Service Provider
project developers, utilities and other
companies within the sector. The UL/DEWI
Group currently operates two wind test sites
in Wilhelmshaven, Germany and at the West
Texas AM University, USA.
123. Introduction of UL/DEWI
A Global Service Provider serving the Wind Energy Industry
DEWI and
DEWI-OCC belong
to the UL family
of companies.
The DEWI Group
comprises:
DEWI:
One of the leading international
performance, measurement,
efficiency, research and
education providers in the field
of wind energy for about 25
years.
UL (Underwriters
Laboratories):
A premier global independent
safety and performance
science company, with more
than 120 years of history.
DEWI-OCC:
Recognised worldwide as
a leading independent
certification body of on-
/offshore wind turbines and
their components.
124. Introduction of UL/DEWI
A Global Service Provider serving the Wind Energy Industry
25 years experience
1,500 clients in 53 countries
636 clients from abroad
180 employees world-wide
ULHeadquarter/Branches (extract)
DEWI Headquarter/Branches
125. DEWI helps stakeholders – developers, investors and operators – to identify the critical
aspects related to wind farm projects through comprehensive one-stop services,
individually tailored and flexibly delivered.
Services Portfolio Over Windfarm Life
5
127. Wind Farm Performance
• Wind farms performance: a key challenge for wind farm operators
• During Operation of the wind farm:
Follow-up and check production and performance of the wind turbines.
• Main aspects to monitor:
• Power performance
• Turbine settings (Yaw alignment, blade angle adjustment, rotor imbalance, etc.)
• Availability and main down times
Reach performance as planned before construction
128. Wind Farm Performance Analysis
Standard approach
Data analysis
On site
measurements
SCADA
data
Error logs
Yaw
alignment
Rotor
Imbalance
Power
curve
Optimized WF performance
130. Wind Farm Performance
Standard Analysis Major drawback is low accuracy of nacelle sensors
Solutions (among others):
Need of more accurate measurement
Met mast
Spinner
anemometer
Nacelle
Mounted LiDAR
Ground
Based LiDAR
132. Nacelle Mounted LiDAR
Measurement
Principle
Technologies Objectives Data analysis
Measurement principle
• Measures remotely the free flowing wind before it
passes through the rotor
Installation
• Installation on the nacelle roof
• Alignment with rotor axis and setting of tilt and roll
• Remote connection and synchronization with
SCADA
Measurement Campaign
• Need of sufficient data set depending on final goal
• Usuall requested measurement duration
• Yaw alignment: 10-15 days
• Nacelle transfer function: 3 to 6 weeks
• Operational power curve: 3 to 6 weeks
Disturbed
flow
Free flow
133. Nacelle Mounted LiDAR
Measurement
Principle
Technologies Objectives Data analysis
Various Manufacturers and technologies
• Leosphère: Wind Iris (2 beams LiDAR)
• ZephIR: ZephIR DM (scanning LiDAR)
• Windar Photonics: WindEye
• Other manufacturers
Applications
• Accuracy and potential applications depends on
the technology of the device.
• For example ZephIR DM and Wind Iris LiDARs
allow the applications mentioned hereafter.
Terrain complexity
• Standard use: for simple terrain
• Complex terrain: so far no industrial solution in
the market
134. Nacelle Mounted LiDAR
Measurement
Principle
Technologies Objectives Data analysis
Yaw alignment
• Measure the difference between the wind
direction and the turbine rotor axis
• Correct Yaw misalignment (if identified)
• Avoid important production losses and undesired
loads
Nacelle transfer function
• Measure the nacelle transfer function
• Application to the nacelle anemometer for further
data analysis and performance analysis
Operational Power Curve
• Check the Operational Power Curve during the
campaign
• Identify where gain of energy production is
possible
The operational power curve and nacelle transfer function
verifications according to IEC 61400-12-1 and IEC 61400-
12-2 requirements do not consider LiDAR measurement
α
135. Nacelle Mounted LiDAR
Measurement
Principle
Technologies Objectives Data analysis
Main input data for analysis
•LiDAR measured data (10 minutes average):
• Wind-speed in front of the rotor (m/s)
• Relative wind direction (°)
•10 minutes SCADA data:
• Ambient temperature (°C)
• Nacelle Position (°)
• Wind-speed nacelle (m/s)
• Power output (kW)
Data filtering
• Filtering according to nacelle position
(unperturbed sectors)
• Filtering of some transitory events
Specific analysis
• Each application is related to specific analysis and
data filtering (see next slides)
137. Nacelle Mounted LiDAR
Yaw alignment
Aim
• Measurement of the difference between the wind direction
and its measurement axis, aligned with the turbine rotor
axis
Data analysis
• Filtering of transitory events and extreme values
• Flow homogeneity and data availability
• Measurement until convergence of misalignment value
Corrective measures
• Adjustment of the yaw angle setting
Outcome
• Reduction of undesired loads
• Optimize the extraction of energy from the wind flow
138. Nacelle Mounted LiDAR
Nacelle transfer function
Aim
• Measure the nacelle transfer function to be applied to the
nacelle wind speed to calculate the theoretical free wind
speed.
Data analysis
• Selection of sector (out of wake from neighboring turbines
and obstacles)
Outcome
• Nacelle transfer function
• Application to the nacelle anemometer wind speed for
further data analysis and performance analysis
The operational power curve and nacelle transfer
function verifications according to IEC 61400-12-1
and IEC 61400-12-2 requirements do not consider
LiDAR measurement
139. Nacelle Mounted LiDAR
Operational Power Curve
Aim
• Measurement of the wind-speed in front of the rotor in
order to check the Operational Power Curve
Data analysis
• Selection of sector (out of wake from neighbouring turbines
and obstacles)
• Air density correction
• Comparison with power curve from SCADA data
Corrective measures
• In case of underperformance identified: investigation of
root cause and actions
Outcome
• Identify range of wind speed where gain of energy
production is possible.
The operational power curve and nacelle transfer
function verifications according to IEC 61400-12-1
and IEC 61400-12-2 requirements do not consider
LiDAR measurement
141. Conclusion
• Nacelle mounted LiDAR allows to gather more accurate data to perform more reliable
analysis of wind turbines performance.
• The 3 mains goals of a nacelle mounted LiDAR measurement campaign are checking of:
• Yaw alignment,
• Nacelle transfer function,
• Operational power curve.
• If underperformance or unacurate settings are identified, correction can be applied in order to :
• Improve performance and production,
• Avoid undesired loads.
• Other applications of Nacelle mounted LiDAR
• Offshore Power Curve Verification
143. Grid Integration, FCAS and
Market Systems.
Kate Summers
Manager, Electrical Engineering Pacific Hydro
WIF
March 2016
144. Focus
• Challenges in the NEM - Frequency Control
• Unpick the stories
• Fact check on the performance of wind farms
• Future aims
K Summers - WIF 2016 2
145. South Australia – RE Integration• Lots of Integration Reports:
• 2011, 2013, 10/2014, 10/2015, 2/2016
• Withdrawal of NPS / Playford, concern over rate of change of frequency.
• Wind Farms make up ~28% of SA generation1 (without retirements)
• Wind Farms are allocated ~ 65% of CPF generator costs
• Frequency control and the excessive cost of frequency control
• Market Systems must integrate with the power system – not redirect it.
• Provision of Ancillary Services requires scrutiny
• Do we get what we are paying for?
K Summers - WIF 2016 3
146. Wind Function Information Flow
Wind
Farm
SCADA
EMS AWEFS
NEMDE
Dispatch
Targets
Dispatch
Assessment
CPF Assessment
CPF
Allocation
There is no doubt about it – its complex!!
ADE
Regulation
Requirements
148. Using Public Data only …
K Summers - WIF 2016 6
• Oakland Hill Wind
Farm across 9th/10th
May 2015
• Oakland oscillating
• Oscillated
completely off for
the entire weekend
153. Conclusion
A lot of work is required to return to basic power system control – the fundamentals are being lost
– FCAS specification of Contingency services needs correcting
– Re-establish control hierarchy – Frequency services must control frequency.
– The push for inertia markets and more interconnector constraints needs to back off until we
correct the errors in the dispatch of FCAS services.
– The FCAS markets needs to be reviewed and barriers to RE participation removed
Renewable Energy
– Forecasts must be accurate
– The wind industry has to improve SCADA data feeds to AEMO
– AEMO need to improve forecast logic and NEMDE integration of forecasts
– Wind turbines can easily provide L6, and L60 services and should look into doing that.
K Summers - WIF 2016 11
154. References:
AER: FCAS prices above $5000 MW - 1 November 2015 (SA)
AEMO: Load shedding in South Australia on Sunday 1 November 2015
AWEFS UIGF Scheduling error_2012 to 2016_FINAL
K Summers - WIF 2016 12
155. Keith Ayotte
Chief Scientist
Windlab Limited
Understanding and Predicting
Topographic Wake Turbulence
Emma Howard
Wind Engineer
Windlab Limited
156. The next fourteen minutes/slides:
A few words about atmospheric boundary layer turbulence
The IEC and turbulence in wind turbine design
A description of topographic wake turbulence
Show that topographic wake turbulence can be described by a simple production-transport-
dissipation model
Describe two ways of modelling topographic wake turbulence.
Show two ways of modelling topographic wake turbulence
An introduction to some open source CFD tools
Show some progress in how we model topographic wake turbulence
157. IEC Turbine Design Curves
Mean wind speed and turbulence probability distributions in wind turbine design.
TI
u
2
v
2
w
2
U
Turbulent Intensity
TI
u
U
Sometimes used
159. l ~ m’s – 100’s m l ~ mm
In the lee of topographyIn the free atmosphere
160. High pressure Low pressure High pressure
Pressure gradientPressure gradient
How can we model topographic wake turbulence?
Hills are in many ways like a ( stalled ) aircraft wing.
161. Two Types of CFD Modelling
RANS
Reynolds Average Navier Stokes (RANS)
- can be done commercially
- many assumptions about length scales
- simple boundary conditions
- treats turbulence cascade in a very simple way
that does not account for all of the length scales
associated with geometry of the hill
162. LES
Large Eddy Simulation (LES)
- prohibitively expensive computationally
- makes far fewer assumptions about length scales
- idealised flows and boundary conditions
- quite naturally reproduces all of the length scales
associated with generation, transport and dissipation
Can we learn some things about the length scales in the flow that allow us to modify our RANS model in a
physically sensible way, to include externally imposed length scales?
We think so. Here’s how.
Two Types of CFD Modelling
163. Start with turbulence kinetic energy and dissipation equations
k
t
U j
k
x j
xl
t
k
k
xl
P
t
U j
x j
xl
t
xl
C1
P
k
C 2
2
k
dk
t
P
d
t
c1
P
k
C 2
2
k
Apply in homogeneous turbulence to get two
ordinary differential equations
k(t) k0
t
t0
n
(t) 0
t
t0
(n 1)
t0 n
k
0
C 2
n 1
n
k
t
U j
k
x j
xl
t
k
k
xl
P(1 ckp
p
xn
)
t
U j
x j
xl
t
xl
C1
P
k
C 2 (1 cp
p
xn
)
2
k
Pope, S.B., 2000, Turbulent Flows, Cambridge
University Press, Cambridge
cp
p
xn
ckp
p
xn
164. Turbulence generated in lee of the hill is directly
dependent upon the strength of the adverse
pressure gradient and the shear at the top of the
hill.
Turbulence is generated in much larger quantities
at larger length scales.
This allows the turbulence to be transported
downwind in the mean flow for much greater
distances before it is dissipated.
What really happens
168. An example of turbulence prediction
across a coastal area.
169. 240 deg 270 deg 300 deg
Thanks for your
attention.
170. CEC Wind Industry Forum 2016
Innovation in Turbine Tower Design
Concrete Towers
Kieren Lewis – Senior Manager, Construction
171. 2
Concrete Towers - is there are place for
them in the Australian Market?
Latest wind turbine technology is around bigger rotors and tall towers. Taller towers
present challenges and opportunities. There is demonstrable evidence internationally
that concrete towers can play a significant part of meeting local content requirements,
assist in achieving a social licence to operate, and be economically superior for both
project proponents and the local community. Whilst high costs in Australia (by global
standards) means that further assessment is required, initial modelling undertaken by
Acciona in Australia suggests that, for the right project and market conditions, concrete
towers may have a positive project impact. Certainly there is a case for maintaining
flexibility during project permitting to allow the option for concrete towers.
172. 3
Safety Moment
What – 12kV UG circuit trip
How – a fencing contractor engaged by a
landowner drilled through a live cable
with a tractor mounted auger
Consequences – moderate (actual) and
catastrophic (potential – near miss)
Why – did not DIAL BEFORE YOU DIG,
misinterpreted warning signs, no JSEA
Outcomes – landowner engagement, site
risk assessment, contractor procedures,
replace/additional signs
173. 4
Overview
ACCIONA – leaders in the wind value chain
Trends – constraints, bigger rotors, taller towers, permits catching up
Why concrete towers?
ACCIONA’s concrete tower solution
Project Comparison – Mt Gellibrand Wind Farm
Conclusions – leave the option open
177. 8
ACCIONA’s Concrete Tower
Patented design
with 20m pre-cast
“keystones”
Keystones are
joined vertically into
sections
Entire tower is post-
tensioned with 6
cable bunches into
the foundation
Small steel adapter
connection on top
section
180. 11
Australian Analysis
Below 100m, steel is more
economical unless other project
factors prevail
Concrete tower costs converge
with steel as quantity increases,
more rapidly at higher tower
heights
Other factors may come into play
• Government schemes / Local
Content (ACT / VIC Auctions)
• Site characteristics
• Manufacturing capacity
• Community support
181. 12
Project Comparison
Mt Gellibrand Wind Farm
Maximum tip height of 150m in DA
Original configuration of 115 x AW1500/82
3 x modifications to 44 x AW3000/125 (87.5m tower)
10% more energy from the same number of WTGs
Positive NPV impact for both 120/140m tower
Tower MW GWh CF
Tower
Cost
NPV
87.5m 132 435 38% - -
120m 132 460 40% 23% 16%
140m 132 477 41% 39% 28%
182. 13
What does it mean?
The market is moving beyond 150m tip heights
Concrete towers show economic and social project benefits internationally
Local analysis confirms improved project economics at 120/140m+
Specific project characteristics (location, size etc.) and/or proximity to
established casting facility impacts steel v concrete equation
Concrete provides direct local content and community benefit supporting
bid requirements and contributing to a social licence to operate
There is a case for maintaining flexibility in DAs to allow concrete towers
183. TransGrid’s Renewable Energy Hub
Mal Coble, Group Manager, Business Diversification
17 March 2016
More than a network
#WIF2016
184. TransGrid's Renewable Energy Hub
About us
Operator and manager of the NSW transmission
network, we connect generators, distributors and
major end users
64,200 GWh moved in 2014/15
12,900 km transmission lines
99 substations
2,300 km optical fibre
We’re more than a network
2 / Grid innovation: the role of transmission in the evolving energy ecosystemTransGrid’s Renewable Energy Hub2 /
Legend
Sydney
185. TransGrid's Renewable Energy Hub
New England
region
NSW
Renewable
Energy Hub
A Renewable Energy Hub could bring more than 700MW in additional connections
3 /
186. TransGrid's Renewable Energy Hub
Title goes here
Stage 1:
Feasibility study
& knowledge
sharing report
Proof of Concept – New England
Identify & implement potential future
renewable hubs
First customer
connection request
Stage 2:
Construction of
Renewable Energy
Hub
4 /
188. TransGrid's Renewable Energy Hub
Network configuration – without a hub
330kV Transmission line
Connection point
Proposed transmission line
Proposed substation
Glen Innes substation
132 kV
Transmission
line
6 /
189. TransGrid's Renewable Energy Hub
Network configuration – with a hub
330kV Transmission line
Connection point
Proposed transmission line
Proposed substation
Glen Innes substation
132 kV
Transmission
line
7 /
190. TransGrid's Renewable Energy Hub
Standalone
connection costs
Hub connection
costs
Overall
cost
saving
Overall
connection
cost for hub
arrangement
Commercial considerations
Cost savings
Risk sharing
Investment returns
Replication
The New England Renewable Hub brings economic benefits
8 /
191. TransGrid's Renewable Energy Hub
Regulatory considerations
There are potential hurdles to
commercial development/funding
of a SENE or a hub concept study
that need to be addressed.
Incentives for a commercial party
to fund for such a study need to
be considered.
Is it a SENE?
9 /
192. TransGrid's Renewable Energy Hub
Community engagement
There is overwhelming broad
community support for these types
of development in the region.
Benefits
New England community:
“We are different”
10 /
193. TransGrid's Renewable Energy Hub
Next steps
> Balranald
> Buronga
> Broken Hill
> Darlington Point
> Griffith
> Parkes
> Tamworth
> Wellington
Visit our stand to find out more
Other possible hub locations
11 /
194. Connection hubs may prove to be an important
ingredient in addressing challenges associated with
increasingly decentralised electricity supply from
renewable sources
196. Overview
2
DECISION MAKER – MINISTER FOR PLANNING
The Minister for Planning is the responsible authority
(decision maker) for all new wind farm applications in
Victoria.
This includes planning permits for transmission
infrastructure
DELWP - PLANNING
• administers all applications and briefs the
Minister for him to determine applications.
• Planning will consult with and work with the
local council regarding all applications
197. Changes to planning controls
3
VC124 – 2 April 2015
Recent change to the planning controls in 2015-16 are:
VC107 – 26 November 2015
• Minister for Planning to decide transmission infrastructure planning permit
applications (including vegetation removal) .
• -Reduced the 2km rule to 1km.
• Minister for Planning to decide all new wind farm planning permit applications.
• allows amendments to existing ‘called in’ planning permits to be considered
without the need for a panel hearing.
VC126 – 28 January 2016
What does it mean?
Do I need to know this?
No, the planning scheme provisions are
most relevant to your application
198. What should be in my application?
4
Your application for a new wind farm must include:
• An application form and the prescribed fee
• Copies of title for all land
• Written consent of all house owners within 1 kilometre of a
turbine
• A planning report that considers the proposal against the
requirements of the planning scheme and the Wind Energy
Facility Guidelines
• Plus – anything else relevant to assessing the impact of your
proposal
• Include peer reviews of key reports: noise, avifauna,
visual impact
Your planning consultant can do this for you
199. What should be in the planning report?
5
Your planning report must demonstrate how your proposal meets
the planning scheme requirements, including:
• State and Local Planning Policy
• Zones and Overlays affecting the land
• Permit triggers for use and development
• Particular provisions in particular
• Clause 52.32 wind energy facilities
• Clause 52.17 native vegetation removal
• Decision guidelines for each permit trigger
• General provisions including:
• Referral authorities Your planning consultant
can do this for you
200. The application process
Lodge
application
• If further information is required it will be requested
Referral and
Notice
• Referrals to authorities identified in planning scheme and CASA
• Views of DELWP environment is sought on avifauna impacts
• The department will work closely with council to ensure council’s input, particularly on local issues.
• Application is advertised by mail, signs, notice in paper
Decision
•Submissions considered
•DELWP Staff make recommendation to the Minister who then determines the application
•Decision can be reviewed at VCAT by objectors
6
201. What about ‘called in’ applications?
7
Some applicants may request that the Minister ‘call
in’ an application under Section 97 of the Planning
and Environment Act 1987
Victoria’s Regional Statement identifies that
applications of state or regional significance may be
called in to fast track decision making
Submissions received following advertising are
referred to a panel hearing
After the panel hearing and receipt of the panel
report the Minister determines the planning permit
application
Decisions made on called in applications are exempt
from 3rd party review (VCAT)
202. How to amend an existing permit?
8
First check if the permit was issued by council or the Minister
and if it was called in
If issued by council: apply
to council to amend the
permit (S72)
If issued by Minister
following a call in: apply to
the Minister to amend the
permit (S97)
Note: if the number of turbines is not increased, and no turbine is moved closer to a
house then:
a) You do not require the written consent of house owners within 1km
b) There are no third party appeal rights (VCAT)
c) The amendment to a called in permit is exempt from being considered at a panel
hearing
203. What should be in my application to amend a permit?
9
Your application to amend a permit should include:
• An application form and fee
• Copies of title for all land
• Written consent of all house owners within 1
kilometre of a turbine (if required)
• Detailed reports that assess the impact of the
changes. Concentrate on the change, don’t
reinvestigate the whole thing.
• Include peer reviews of key reports such as
noise, flora and fauna impacts, visual impact.
• Plus – anything else relevant to assessing the
impact of your proposal
Before you lodge, consult
with:
referral authorities
CASA
DELWP environment
(avifauna and veg
removal)
Council and
the local community
204. Tips for applicants?
10
• Consult before you lodge
• Identify referral authorities and engage with them early (before you lodge).
Also engage with CASA, DELWP environment (avifauna impacts)
• Engage with council and community (no surprises)
• Have an on-site quarry to limit traffic impacts
• Go to every effort to limit vegetation removal
• Consider the Brolga Guidelines and design accordingly
• Deal with issues before you lodge, don’t just ask for them to be permit
conditions
• Make sure all your consultant reports include an executive summary that
clearly spells out the findings, and is focussed for planning consumption
Use a planning consultant
205. More tips
When submitting documents for endorsement under permit conditions:
• Always use the permit as a checklist
• The planners will be assessing your plans / documents against the permit
conditions
• Check that you have met each part of each condition before you lodge
them
• Include a covering letter or report that spells out how you meet the
requirements of each condition, and where to locate that specific item in
the plan / document
• It saves time if you do these things
11
Your planning consultant
can do this for you
206. What else?
12
The current state government has repeatedly expressed its
commitment to renewable energy and the wind industry.
Read Victoria’s Renewable Energy Action Plan August 2015 and
follow developments leading from it.
The target is for 20% of Victoria’s energy to come from
renewables by 2020.
There is political support, but you must still prepare a solid,
thorough and justified application to obtain a permit.
And…. Use a planning consultant.
Questions?
207. SLIDE 1
GRID INTEGRATION
March 2016
PRESENTED BY NICOLA FALCON
GROUP MANAGER, PLANNING
The changing role of transmission in Australia’s energy future
208. SLIDE 2
AGENDA SLIDE
1. About AEMO
2. Network Development
3. Risk of Local Congestion
4. AEMO’s Planning Process
5. Investment Triggers and Risks
6. 2016 Victorian Annual Planning Report (VAPR)
7. Integrating Renewables in the VAPR
8. Questions
209. SLIDE 3
ABOUT AEMO
• Australian Energy Market Operator (AEMO).
• Our vision “Energy security for all Australians.”
• AEMO is fuel and technology neutral.
o Generation expansion plan will consider how Australia
may cut carbon emissions by at least 26 per cent of
2005 levels by 2030.
• Guided by the National Electricity / Gas Objectives:
o To promote efficient investment in, and efficient
operation and use of, electricity services for the long
term interests of consumers
211. SLIDE 5
IMPORTANCE OF GENERATION LOCATION
Biomass Large-scale PV Wind Open Cycle Gas Turbine
Additional generation location by 2024-25 – Gradual Evolution scenario (left) and sensitivity
• Widespread wind and solar resources could enable new generation to
connect where there is spare network capacity
• But concentration of generation can lead to local network limitations
212. SLIDE 6
RISK OF LOCAL CONGESTION
North-west Victoria (case study)
• Wind farm developers interested in
connecting to the Ballarat-Waubra-
Horsham 220 kV transmission line (BATS-
WBTS-HOTS).
• this line currently connects Waubra Wind
Farm (190MW) and Ararat wind farm
(240MW) will be commissioned in 2017.
• additional wind farms connecting will
increase the risk of exceeding the thermal
limit of the line between BATS and WBTS.
• increasing non-synchronous generation will
increase the potential of instability in the
region.
213. SLIDE 7
CHALLENGES CAUSED BY LOCAL
CONGESTION
Load = 200MWGeneration cost = $0/MWh
200MW capacity
150MW dispatched
Generation cost = $10/MWh
200MW capacity
50MW dispatched
100% loaded
Short Circuit Ratio
214. SLIDE 8
RISK OF GETTING CONSTRAINED
• The generator that will be constrained depends on:
o Variable operational conditions
o Economic considerations
o The location of each wind farm relative to the
constraint
• Will network capacity be augmented?
o Augmentation is only justified if net market benefits
are sufficient
• Generators are not entitled to reserved network capacity
215. SLIDE 9
PLANNING PROCESS
Phase 1 – Exploratory (covered in 2016 VAPR)
• Screening studies to identify potential limitations and their timing (based on
MW connected).
• Scenario studies on future triggers that will worsen limitation.
• Market modelling to identify potential market impact and potential benefits for
alleviating these limitations.
Phase 2 – Scoping (limited coverage in 2016 VAPR)
• High-level studies to assess each solution’s technical effectiveness, cost
estimate, and potential benefits across a range of scenarios.
Phase 1 -
Exploratory
Phase 2 -
Scoping
Phase 3 –
Pre-
feasibility
Phase 4 –
Feasibility
216. SLIDE 10
INVESTMENT TRIGGERS AND RISKS
Average fuel costs in the NEM from 2016-2025
Changing generation mix – Rapid Transformation (2015 NTNDP)
0
10,000
20,000
30,000
40,000
50,000
60,000
70,000
80,000
90,000
2015-16 2020-21 2025-26 2030-31 2034-35
InstalledCapacity(MW)
Black Coal Brown Coal Hydro Liquid Fuel Natural Gas
Large Scale PV Wind Biomass Rooftop PV
0
2
4
6
8
10
12
Brown Coal Black Coal Coal Seam
Methane
Natural Gas
Pipeline
Diesel
$/GJ
217. SLIDE 11
2016 VICTORIAN ANNUAL PLANNING
REPORT
• The Victorian Annual Planning Report will be published
in June 2016
• Will explore wind + potential augmentation options as
part of a case study in North-West Victoria
• Interactive map that illustrates the hotspot area of future
renewable generation and other information (limits,
possible connection capacity)
221. SO WHERE ARE WE AT ??
So are Wind Turbines a Health Problem or not?
There have been at 24 reviews that have shown that there is no
evidence of direct health effects
The NHMRC investigated this question and concluded:
After careful consideration and deliberation of the body of
evidence, NHMRC concludes that there is currently no consistent
evidence that wind farms cause adverse health effects in humans.
BUT
Given the poor quality of current direct evidence and the concern
expressed by some members of the community, high quality
research into possible health effects of wind farms, particularly
within 1,500 m is warranted.
.
222. HEALTH CANADA STUDY
The objectives of the study were to:
Investigate the prevalence of health effects or health indicators among a
sample of Canadians exposed to WTN using both self-reported and objectively
measured health outcomes;
Investigate the contribution of LFN and infrasound from wind turbines as a
potential contributing factor towards adverse community reaction.
The following were not found to be associated with WTN exposure:
self-reported sleep (e.g., general disturbance, use of sleep medication,
diagnosed sleep disorders);
self-reported illnesses (e.g., dizziness, tinnitus, prevalence of frequent
migraines and headaches) and chronic health conditions (e.g., heart disease,
high blood pressure and diabetes); and
self-reported perceived stress and quality of life.
223. ENERGY AND POLICY INSTITUTE REVIEW OF
COURT CASES
Since 1998, 49 hearings have been held under rules of legal evidence
in at least five English-speaking countries and four types of courts
regarding wind energy, noise, and health.
Forty-eight assessed the evidence and found no potential for harm to
human health.
There was one outlier –Falmouth!
Courts in Denmark, Germany and the Netherlands have also found no
connection between wind turbines and health issues per reports, but
the records are not in English.
224. REVIEW OF COURT CASES
Court cases jumped dramatically after Dr. Nina Pierpont’s self-
published a book alleging health risks from wind turbines based on
phone interviews with a self-selected and very small number of
people who blamed them for commonly experienced symptoms.
Canada is the centre of wind farm health-related court challenges,
with 17 separate hearings
Mainly in Ontario, with 14 Environmental Review Tribunals (ERT)
testing the evidence and the relative experts, as well as two higher
court cases.
All Canadian courts found that wind farms would not and do not
cause health impacts with proper setbacks in place
225. CASES IN AUSTRALIA
Australia with 10 cases.
Victoria with seven civil suits.
South Australia and New South Wales saw three cases in
their environment and resource courts.
All Australian cases found that wind farms would not
cause health impacts with proper setbacks in place.
227. CASES IN THE USA
The United States saw eight court.
Seven cases found no harm from wind energy with the proper setbacks
currently in place
The USA has the only case where a wind farm was considered to have
caused harm.
This case was brought by a single family near a pair of wind farms
erected on the municipal wastewater treatment plant by the town of
Falmouth, Massachusetts. The judgment includes the statement that
dental harm occurred, along with other types of medical ailments.
This single small wind farm is referenced worldwide by anti-wind
advocacy groups as if it is representative of wind health court cases
instead of a unique outlier
228. CASES IN NEW ZEALAND
New Zealand had five environmental and civil hearings over wind
energy, noise and health
Only one case in New Zealand went against a wind farm, the Te Rere
Hau wind project, and that was only because noise was greater than
anticipated, not because the wind noise was above standards or
harmful to human health.
This case is widely misrepresented and selectively quoted by anti-
wind campaigning organizations such as the Waubra Foundation and
National Wind Watch
229. European Platform Against Windfarms
961 Member organizations from 30 European countries
AUSTRALIA 1
MEXICO 3
EU 3
NORWAY 4
CANADA 10
USA 13
SWITZERLAND 16
DENMARK 18
IRELAND 27
BELGIUM 29
UK 120
GERMANY 173
FRANCE 381
BUT eg Belgium 29 listed, only 8 were working and of those, 3
were inactive, making 5 still active (Simon Chapman 2016)
230. AUSTRALIA’S WIND FARM COMMISSIONER
The Wind Farm Commissioner is an independent role reporting
directly to the Minister for the Environment.
There are no formal powers and the WFC does not displace the
responsibilities of state jurisdictions.
The WFC is meant to operate “based on the effectiveness of my
relationships with a wide and diverse range of stakeholders from all
levels of government, industry and the community”.
Currently, the WFC has a chief of staff, an administrative assistant on
loan from the department. He intends to hire a complaint-handling
manager and a research officer.
So far, 42 complaints about 12 WF’s. 5 Operational, 7 in development.
For the wind farms that have been constructed, typically issues are
again around noise, health effects, turbine configurations, turbine
height and economic loss.
231. ENGAGEMENT and COMPLAINT HANDLING
In his recent evidence, Mr Dyer stated:
One of the improvement opportunities that I have seen from
anecdotal discussions is to help those agencies and stakeholders
you have just described to improve their complaint handling
processes. It is not just a matter of capturing a complaint; you
need to do something with it.
I think many of the players in the industry and supporting the
industry could further improve their complaint handling
processes, which would then take a load off us
.
232. LFN & IS Hearing Thresholds
Watanabe & Moller (1990)
233. IS & LFN COMPARISON URBAN
SA EPA/Resonate (2013)
234. SENATE SELECT COMMITTEE ON WIND TURBINES
Broner in evidence
“So to summarize, I believe that IS is not the source of
any complaints due to wind turbine noise.
I believe that LF audible noise may be a possible source
and that the current recent research shows that wind
turbine noise does not cause health impacts when A
weighted criteria are met.
I believe that A-weighted noise level criteria are therefore
adequate to describe wind turbine noise. And I note that
both the Canadian and Japanese work found that the use
of A weighting was validated”.
.
235. ANNOYANCE RESPONSE
Activities Disturbed
Eg Reading,
TV viewing
Situational
Eg Season, time of day
Acoustical
Eg Intensity, frequency
Demographic,
biographic
and sociological
Eg Age, sex,
income
Other
Eg Expectation,
previous experience
Psychological
Eg Personality, sensitivity
236. How Important is the Acoustic Stimulus Alone?
For a community, % Variance in response explained
20 – 30%.
For an individual, % Variance in response explained
10 – 15%
238. ONTARIO TO GET ANOTHER STUDY!
More Ontario wind-health investigation: "The Huron County Health
Unit (HCHU) will be conducting an investigation into the reported
health effects from wind turbines. This investigation is in response to
feedback from numerous Huron County residents reporting negative
health impacts resulting from living in close proximity to the massive
apparatuses designed to capture energy from wind.
The study will consist of two phases:
The first phase will include a launch of an online survey in May to
collect information in regard to the number of complaints and/or
concerns of residents.
The second phase of the investigation, according to Ryan, may involve
acoustic testing both outside and inside affected homes."
.
241. www.ehpartners.com.au
Wind Farm Implementation Guidelines
• Construction Environmental Management Plan
– Identify the risks
– List the actions to be taken
– Capture conditions of approval / commitments
– Appoint a person responsible for implementation
2
242. www.ehpartners.com.au
Wind Farm Development Guidelines
• Construction Environmental Management Plan
– Must be prepared
– Must be endorsed by the relevant authority
– Must identify person to whom incidents, non-
conformances and complaints should be made
3
243. www.ehpartners.com.au
Wind Farm Development Guidelines
• Construction Environmental Management Plan
– Should be ‘signed off’
– Should include monitoring
– Should include a compliance regime
– Should identify a person from the company who is
responsible for implementation
4
244. www.ehpartners.com.au
Guidelines for Wind Farm
• Construction Environmental Management Plan
– State how any adverse impacts will be managed
– Expert advice
– Best practice techniques
– Project staging and phasing
5
245. www.ehpartners.com.au
Wind Farm State Code
• Construction Environmental Management Plan
– Construction Erosion and Sediment Control Plan
• Certified by a RPEQ
– Construction Traffic Management Plan
• Certified by a RPEQ
6
246. www.ehpartners.com.au
Wind Farm Approval Conditions
• Environmental Representative
– Suitably qualified and experienced person
– Independent of design, construction & operations
– Oversee the implementation of the CEMP
– Report on any non-compliances against the CEMP
7
247. www.ehpartners.com.au
What is Best Practice?
• Satisfactory CEMP
– Start of the project
• CEMP revision
– During the project
• CEMP implementation
– Independent compliance monitoring and auditing
8
248. www.ehpartners.com.au
Achieving Best Practice
Have the CEMP prepared by a Registered
Professional / Certified Practitioner.
Have the CEMP reviewed by a Registered
Professional / Certified Practitioner.
Have the implementation of the CEMP
monitored by a Registered Professional /
Certified Practitioner who is not an employee
of the design, construction or operational
entities.
9
249. www.ehpartners.com.au
Registered Environmental Professional
• Completed a degree, higher degree or
graduate diploma and have at least two years’
experience in an area of environmental
practice.
• At least five years’ experience in an area of
environmental practice.
10
250. www.ehpartners.com.au
Certified Environmental Practitioner
• An environment-related degree.
• Five years of full time equivalent
experience in the functional areas
of environmental practice during
the last ten years.
• Ongoing commitment to training
and professional improvement.
• Respected, competent, ethical and
an active member of the
profession.
11
253. Introduction
Who is Gamesa?
Low wind site analysis
5 Challenges for low wind success
I. Maintain low power density
II. Cost efficient low-wind rotors
III. Cost efficient tall towers
IV. Cost efficient manufacturing platforms
V. Efficient BOP and Logistics
What to remember
254. 1994 commenced making turbines
Home base in Pamplona, Spain
Total installed worldwide 35 GW
Turbines under O & M 21 GW
Projects developed 7.5 GW
Development pipeline 12.5 GW
Installed turbines in 53 countries
Top 5 in worldwide sales in 2015
Top 5 total installed in world
Commenced G80 2MW in 2002
Over 22 GW of 2MW platform installed
G114 rated best turbine 2015
(2-3MW class: Wind Power Monthly)
255. Low wind sites expected to be
close to 50% worldwide from
2016 to 2020
The shift into auction schemes
will make tougher for these
sites to compete Vs. other
renewable technologies
New technological approach
needed to reduce this site’s
Cost of Energy
256. Hub height relevant in high shear sites
Clear trend towards low power density
Best energy gain from rotor diameter
MW relevant in high speed sites
Rotor Dia. Swept Area Area Increase
90m 6,362m2
110m 7,854m2 49%
130m 13,273m2 109%
0
5000
10000
15000
20000
25000
30 40 50 60 70 80 90 100 110 120 130 140 150 160
257. Increasing power while maintaining
power density should lead to an
increase cost of energy, but…
New technology developments and
control strategies are leading to
loads control shifting this trend
Rotor Dia. Output Power Density
90m 2MW 314 W/m2
114m 2MW 196 W/m2
126m 2.5MW 200 W/m2
132m 3.3MW 241 W/m2
258. 106m
114m
126m
At 8m/s around 500kW, or
40%, extra power is produced
from 10m more blade length
Rotor
dia.
(m)
Power
density
(W/m2)
Rotor
size
decrease
Power
density
decrease
126 200 0% 0%
114 245 -10% -22%
106 283 -16% -41%
260. Infusion technology: fiberglass reinforced
with epoxy resin
Low noise airfoils and adjusted gearbox ratio
to get reduced sound emission level
High absolute thickness at root sections to
achieve the minimum mass/cost blade
Mid-sections chord alleviation to reduce
maximum loads
Maximum airfoil glide ratio at mid/outer
sections
Shear WebsCaps
261.
262. Over 120 m site-to-site solutions
Standard steel towers
Sectional Tubular Steel
Hybrid #1: Pre-cast concrete +
steel
Hybrid #2: Pedestal + steel
Hybrid #3: Cast-in-place concrete
+ steel
Up to 120 m: Tubular steel towers are usually cost efficient worldwide… currently
263. High commonalities between Class II, Class III & Class IV:
Common main components
Optimized load path adapted to each site
Blade
Pitch system
Main shaft
Gearbox
Yawing system
Tower
Foundation
264. New foundation concepts
optimized site by site for low wind
New efficient on-site pedestals
optimizing production in low wind
sites
New logistics for long blades to
reduce roads and platforms
Innovative crane solutions
Continuous improvement through
experience
265.
266. Low power density is required to maximise cost effective
energy production from low wind sites
Optimisation of all components, including BOP, is
necessary to ensure the cost of energy is low
Seek planning permits with no rotor restrictions to allow
for maximum benefit from overall tip height
268. Wind turbine sound power testing
Wind Industry Forum, 17 March 2016
Tom Evans
Associate Director
269. Outline
What is sound power testing?
Why do we do it?
How do we do it?
What to be aware of
Receptor guarantees vs sound power guarantees
17 March 2016 Slide 2
270. Sound power testing
• Measurements to determine the sound power level
of an individual turbine
• Sound power level is distance/site independent
measure of sound output of a turbine
• Measure downwind at approx. 130 m from turbine
across suitable range of wind speeds
• Analyse measured levels (controlling for known
factors) to determine sound power level
• May also include tonality, amplitude modulation and
impulsivity tests
17 March 2016 Slide 3
271. Sound power vs sound pressure
• Sound power level is a measure of the sound emitted by a source that is
independent of distance. Units: dB re 10-12 W.
• Sound pressure level is the actual sound level at a particular distance/position
from a source. Units: dB re 20 𝜇Pa.
• Sound pressure level is dependent on sound power (and other factors).
• From a sound power level for turbines at a site, the sound pressure level can be
predicted considering other relevant factors such as site layout, distance and
topography.
• Therefore, sound power can be determined from sound pressure measurements
near to the source if we can control other factors – sound power testing.
17 March 2016 Slide 4
272. Why do sound power testing?
• Provides a non site dependent (and therefore transferable) measure of the noise
produced by a particular turbine model.
• Assess compliance with contractual guarantees provided by OEM.
• Assessing site compliance based on sound power – not currently done in Australia
but is in parts of Europe.
• Investigate Special Audible Characteristics – normally tonality.
17 March 2016 Slide 5
273. How do we do it?
• Relevant standard is IEC 61400-11 Wind turbines – Acoustic noise measurement
techniques. Current version is Edition 3 (2012) although many Australian
contracts will still refer to Edition 2.1 (2006).
• Measure downwind of turbine at hub height + ½ diameter using a microphone laid
flat on an acoustically reflective board:
• The ground board is used to provide a consistent reflection from the ground
between sites.
17 March 2016 Slide 6
274. What does the Standard require?
• Wind speeds of 0.8-1.3x the speed at 85% rated power (2012).
• Measurements in 10-second intervals with at least 10 data points
required for each half-integer wind speed.
• Noise with turbine ON to be at least 3 dB higher than with it OFF
across frequency range – normally have to switch off nearest
turbine.
• Same amount of data points required with turbine OFF as with
turbine ON.
• Downwind ±15º only. Optional crosswind and upwind positions
provided but rarely used.
• Allowable measurement angle to turbine hub of 25 to 40º.
17 March 2016 Slide 7
UPWIND
DOWNWIND